Frying your avionics
To those of you who have a circuit breaker between your alternator's
output and your main buss, here's a wonderful way to fry your present old avionics so you can replace them with new ones. This is a real help in justifying new avionics to your significant other! If your alternator field-circuit-breaker is connected to your main buss, then if your alternator breaker opens, either through an overload or manually, your main buss voltage will drop. The regulator, sensing this, will increase the alternator's field current. 'Course, there is no load on the alternator, so its voltage will rise. Eventually, in a few milliseconds, the regulator will be pumping maximum current through the field. Since we drive our alternators at 7000-9000 rpm, the alternator will put out well in excess of 100 volts. Closing through the alternator breaker will put this high voltage on your buss. Your over-voltage protector, if present, will shut off the field supply, but by the time the field collapses, the damage will have been done. Here's two things you can do to prevent this and keep your old avionics. Any time your alternator breaker opens, pull your field breaker before restoring the alternator's breaker. If you don't want to depend on your memory in a time of stress, rewire your field circuit breaker to the alternator side of the alternator breaker. That way the alternator's field will serve as the alternator load and the regulator will be sensing the alternator output, thus keeping it in regulation. If you don't think this scenario could actually take place, I challenge you to do this test on your plane at cruise rpm with lots of avionics load and prove me wrong! |
#2
|
|||
|
|||
Frying your avionics
I challenge you to
do this test on your plane at cruise rpm with lots of avionics load and prove me wrong! That's what overvoltage protection is made for : in the airplane I built, within a few milliseconds, the OV relay opens and disconnects the alternator from the ship's circuit. Regards, Gilles Thesee Grenoble, France http://contrails.free.fr |
#3
|
|||
|
|||
Frying your avionics
GTH wrote:
I challenge you to do this test on your plane at cruise rpm with lots of avionics load and prove me wrong! That's what overvoltage protection is made for : in the airplane I built, within a few milliseconds, the OV relay opens and disconnects the alternator from the ship's circuit. Regards, Gilles Thesee Grenoble, France http://contrails.free.fr Well, yeahbut... Ellipse's method avoids the situation in the first place... |
#4
|
|||
|
|||
Frying your avionics
That's what overvoltage protection is made for : .... Well, yeahbut... Ellipse's method avoids the situation in the first place... The Ellipse's method is just for the load dump case, with a perfectly working voltage regulator. Now, what if it is the regulator that goes berserk ? An overvoltage protection is intended to catch ANY OV condition, regardless of it's cause. Regards, Gilles Thesee Grenoble, France http://contrails.free.fr |
#5
|
|||
|
|||
Frying your avionics
cavelamb wrote:
GTH wrote: I challenge you to do this test on your plane at cruise rpm with lots of avionics load and prove me wrong! That's what overvoltage protection is made for : in the airplane I built, within a few milliseconds, the OV relay opens and disconnects the alternator from the ship's circuit. Regards, Gilles Thesee Grenoble, France http://contrails.free.fr Well, yeahbut... Ellipse's method avoids the situation in the first place... Having a storage battery in the circuit avoids the situation too. The battery, barring bad connections, will soak up the initial surge. The overvoltage protection device is unlikely to trip in Ellipse's scenario, because it won't need to. |
#6
|
|||
|
|||
Frying your avionics
Having a storage battery in the circuit avoids the situation too. The battery, barring bad connections, will soak up the initial surge. Yes, the initial surge. And then...? The overvoltage protection device is unlikely to trip in Ellipse's scenario, because it won't need to. ?? Can't figure out that one. OV is OV, and the avionics pay no mind as to the original cause : zap all the same. It is a good thing to try to fool proof an architecture. But OV protection is there to protect against even things that should not happen. You'd be surprised at the number of things that happen in aviation, and yet should not happen : empty tanks, wheels up landings, popped breakers, fried radios, engine failures, accidents... You may wish to have a peek at www.aeroelectric.com. The load dump scenario has been covered extensively. Regards, Gilles Thesee Grenoble, France http://contrails.free.fr |
#7
|
|||
|
|||
Frying your avionics
GTH wrote: I challenge you to do this test on your plane at cruise rpm with lots of avionics load and prove me wrong! That's what overvoltage protection is made for : in the airplane I built, within a few milliseconds, the OV relay opens and disconnects the alternator from the ship's circuit. Regards, Gilles Thesee Grenoble, France http://contrails.free.fr Hi, Gilles! Do you know all the time-constants of the over-voltage protection loop? You say your OV has a relay which opens; a relay can take 20-60msec to drop out, especially if you have a diode across the coil for inductive transients. What is the L/R time-constant of your alternator's field when fully charged? Do you know? Most of the OV circuits I'm familiar with use a solid-state device, such as an SCR, which is triggered on in a transient that then shorts out the field supply source, causing its circuit breaker to open. What is the time-constant of the SCR's trigger circuit to reduce nuisance triggers from short transients; do you know? Do you also know how long it takes for the field circuit breaker to open? I wrote this posting to make you people aware of a possible failure mechanism in your plane's charging system that could have disastrous results with your avionics. If you wish to dismiss this warning, that is your prerogative. But please, if this situation ever happens to you, pull the field breaker before closing the alternator through! Paul |
#8
|
|||
|
|||
Frying your avionics
Hi Paul,
If you wish to dismiss this warning, that is your prerogative. But please, if this situation ever happens to you, pull the field breaker before closing the alternator through! Read again, I didn't dismiss your load dump issue and proposed solution. I was trying to convey that your suggestion is valid for "normal" cases, and that an overvoltage protection should be included in the ship's architecture to take care of *any* OV condition, including voltage regulator runaway. Best regards, Gilles http://contrails.free.fr |
#9
|
|||
|
|||
Frying your avionics
GTH wrote:
Having a storage battery in the circuit avoids the situation too. The battery, barring bad connections, will soak up the initial surge. Yes, the initial surge. And then...? The overvoltage protection device is unlikely to trip in Ellipse's scenario, because it won't need to. ?? Can't figure out that one. OV is OV, and the avionics pay no mind as to the original cause : zap all the same. It is a good thing to try to fool proof an architecture. But OV protection is there to protect against even things that should not happen. You'd be surprised at the number of things that happen in aviation, and yet should not happen : empty tanks, wheels up landings, popped breakers, fried radios, engine failures, accidents... You may wish to have a peek at www.aeroelectric.com. The load dump scenario has been covered extensively. Regards, Gilles Thesee Grenoble, France http://contrails.free.fr Upon your advice, I peeked at the link. At http://www.aeroelectric.com/articles/spike.pdf Mr. Nuckolls makes exactly the same point as my previous post. Page 2, last paragraph. Mr. Nuckolls and I seem to have quite a bit in common. I, like him, have been poking around aircraft avionics and electrical systems for over thirty years. Currently I'm doing my best to assure the integrity and reliability of avionics and electrical systems in a well-known French-designed line of business jets. I agree with you that overvoltage protection is necessary in an electrical system using and alternator as a power source. I agree with Mr. Nuckolls that most load-dump fears are unfounded, and that a system using a well-designed regulator, effective overvoltage protection, a well-maintained battery, and good wiring design and installation will protect today's avionic systems quite well. Adding additional protection devices or following Ellipse's recommendation carry their own subtle hazards. My point in my first post was that the battery would absorb the initial transient in Ellipse's scenario. The system voltage would never reach the level required to trip the overvoltage protection. If the battery or its wiring were in poor condition, then the overvoltage protection device could trip. Today's radios would not be threatened in either event. Over the last thirty years, I've seen many avionics systems damaged by lightning. I've seen a few damaged by reversed polarity, from improper battery or alternator installation. I've never seen significant damage from load-dump surges. |
#10
|
|||
|
|||
Frying your avionics
ELIPPSE wrote:
GTH wrote: I challenge you to do this test on your plane at cruise rpm with lots of avionics load and prove me wrong! That's what overvoltage protection is made for : in the airplane I built, within a few milliseconds, the OV relay opens and disconnects the alternator from the ship's circuit. Regards, Gilles Thesee Grenoble, France http://contrails.free.fr Hi, Gilles! Do you know all the time-constants of the over-voltage protection loop? You say your OV has a relay which opens; a relay can take 20-60msec to drop out, especially if you have a diode across the coil for inductive transients. What is the L/R time-constant of your alternator's field when fully charged? Do you know? Most of the OV circuits I'm familiar with use a solid-state device, such as an SCR, which is triggered on in a transient that then shorts out the field supply source, causing its circuit breaker to open. What is the time-constant of the SCR's trigger circuit to reduce nuisance triggers from short transients; do you know? Do you also know how long it takes for the field circuit breaker to open? I wrote this posting to make you people aware of a possible failure mechanism in your plane's charging system that could have disastrous results with your avionics. If you wish to dismiss this warning, that is your prerogative. But please, if this situation ever happens to you, pull the field breaker before closing the alternator through! Paul Paul, have you ever tried to reset a 50, 70, or 100-amp circuit breaker in flight? In the few cases I've seen when such breakers have tripped, the crews were unable to reset them. We reset them on the ground, using a soft mallet. I remember one airframe manufacture putting the alternator output circuit breaker in the floor beneath the pilot's feet. That allowed the pilot to stamp his foot on it to reset it. How much experience do you have with aircraft electrical systems, Paul? |
|
Thread Tools | |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Thread Starter | Forum | Replies | Last Post |
IGC-approval issued for EW Avionics microRecorder | Ian Strachan | Soaring | 0 | June 11th 06 05:52 PM |
Has Anyone Used The "Approach Sport Hub Avionics Wiring Systems"? | three-eight-hotel | Owning | 7 | June 1st 06 03:28 PM |
time for avionics upgrade... | kontiki | Owning | 12 | December 11th 04 06:15 PM |
Used Avionics | O. Sami Saydjari | Instrument Flight Rules | 40 | December 2nd 03 02:53 PM |