![]() "Morgans" wrote in message ... | | "John Ammeter" wrote in message | ... | Why does everyone think the voltage is 110/220?? | | If that actually was the voltage you had in your house you'd be very unhappy. | The nominal voltage is 118/236 with a +/- 5% range so you can see that 110/220 | is actually outside the acceptable range. | | Well, duh, John! | | Why is a car called a car? | | People (except you and a few others) don't really care what comes squirting out | of their wall plugs, and what to call it, as long as it makes things work. | | It isn't 120/240 either. It is way too awkward to call it 118/236, even though | that is most accurate. Calling it 110/220 gets the idea across... Let the | electrical engineers and others that get hung up on exactly what it is, figure | out how to fight convention. | | To me, it's still 110/220. | | Now, let's get really weird, and figure out what comes out of the plugs at my | school. Three phase, split off to use single phase, now is it Delta or Y? 95% | of the people in the US don't know and don't care. What will they call that | 208? | -- | Jim in NC | According to my fuzzy memory Delta is 208 and since there isn't a neutral or center reference 110 is not available. Y configuration gives you 220 from leg to leg while from each leg to the common center (Neutral) gives you 110. From there you go to how the transformers are configured, I.E. Delta/Delta or Delta/Wye or Wye/Delta. All of which I do not remember how each effects the voltage result. -- Jarhead ----== Posted via Newsfeeds.Com - Unlimited-Unrestricted-Secure Usenet News==---- http://www.newsfeeds.com The #1 Newsgroup Service in the World! 120,000+ Newsgroups ----= East and West-Coast Server Farms - Total Privacy via Encryption =---- |
#12
|
|||
|
|||
![]() It isn't 120/240 either. It is way too awkward to call it 118/236, even though that is most accurate. Calling it 110/220 gets the idea across... Let the electrical engineers and others that get hung up on exactly what it is, figure out how to fight convention. To me, it's still 110/220. I call it that as well; but I have seen 125. Now, let's get really weird, and figure out what comes out of the plugs at my school. Three phase, split off to use single phase, now is it Delta or Y? 95% of the people in the US don't know and don't care. What will they call that 208? I would but that figure closer to 99.5% I think that's unfortunate, since the easiest way to save money and energy at the same time is to run motors on three phase power; and three phase Y is the only place you'll ever see anything properly called 208 volts. BTW, in my neck of the woods, if you were a major account, you used to get only open delta unless you paid for the installation of closed delta--and it was well worth the price! Peter |
#13
|
|||
|
|||
![]() John Ammeter wrote: Why does everyone think the voltage is 110/220?? If that actually was the voltage you had in your house you'd be very unhappy. The nominal voltage is 118/236 with a +/- 5% range so you can see that 110/220 is actually outside the acceptable range. John actually in my travels, ive seen 90-140 volts nominal for the "standard" 110V outlet. so it is a bit more than 5% tolerance |
#14
|
|||
|
|||
![]()
The service you describe is 120/208V. In the industry where I worked we
called it "Network"... 120/208 3 phase is only used in high density or commercial areas where the utility has a need for 3 phase for elevators, motors, etc. It's a Y configuration with 120 degrees between the phases. Now, out in the hinterlands, the normal configuration is a 120/240 delta setup. If you want 3 phase there it's a 3 phase delta. In Seattle, most apartments are 120/208 and most private homes are 120/240, both single phase. A problem happens when a condo/apartment dweller replaces his electric range with one he bought at a garage sale or an appliance dealer that doesn't ask the right questions of the buyer. What do you think happens when you operate a 240 volt device on 208 volts?? Now you know more than you ever wanted to know... amaze and confound your friends with your newfound knowledge... John Morgans wrote: "John Ammeter" wrote in message ... Why does everyone think the voltage is 110/220?? If that actually was the voltage you had in your house you'd be very unhappy. The nominal voltage is 118/236 with a +/- 5% range so you can see that 110/220 is actually outside the acceptable range. Well, duh, John! Why is a car called a car? People (except you and a few others) don't really care what comes squirting out of their wall plugs, and what to call it, as long as it makes things work. It isn't 120/240 either. It is way too awkward to call it 118/236, even though that is most accurate. Calling it 110/220 gets the idea across... Let the electrical engineers and others that get hung up on exactly what it is, figure out how to fight convention. To me, it's still 110/220. Now, let's get really weird, and figure out what comes out of the plugs at my school. Three phase, split off to use single phase, now is it Delta or Y? 95% of the people in the US don't know and don't care. What will they call that 208? |
#15
|
|||
|
|||
![]()
Did you ever have your linemen wire up the tickler backwards?? That
gets real interesting when the voltage should be 240/480 open delta. I had a job where they needed 3 phase for the elevator and only delta was provided. Thank God it was a 120/240 system because when I wiggied the voltage at the socket I found over 420 volts (I don't recall the exact voltage) from one leg to the other. If it had been a 240/480 service that would have been 840 volts... considered "high voltage" and decidedly dangerous to the operator, namely ME. I used that situation on a Test that I was writing for our Utility. Strangely, only a few people got the question right. We hired a couple of those fellows. John Peter Dohm wrote: It isn't 120/240 either. It is way too awkward to call it 118/236, even though that is most accurate. Calling it 110/220 gets the idea across... Let the electrical engineers and others that get hung up on exactly what it is, figure out how to fight convention. To me, it's still 110/220. I call it that as well; but I have seen 125. Now, let's get really weird, and figure out what comes out of the plugs at my school. Three phase, split off to use single phase, now is it Delta or Y? 95% of the people in the US don't know and don't care. What will they call that 208? I would but that figure closer to 99.5% I think that's unfortunate, since the easiest way to save money and energy at the same time is to run motors on three phase power; and three phase Y is the only place you'll ever see anything properly called 208 volts. BTW, in my neck of the woods, if you were a major account, you used to get only open delta unless you paid for the installation of closed delta--and it was well worth the price! Peter |
#16
|
|||
|
|||
![]()
On Fri, 17 Nov 2006 19:08:34 -0800, John Ammeter
wrote: Why does everyone think the voltage is 110/220?? If that actually was the voltage you had in your house you'd be very unhappy. The nominal voltage is 118/236 with a +/- 5% range so you can see that 110/220 is actually outside the acceptable range. John Officially here it is 115/230 and right now it's 119/238 Morgans wrote: " wrote Which is why they wire them for 220. It can be a lot. If you can get 220v to the location, you will be a happy camper. I have such an air compressor, and it likes 220 the best. g It starts quicker, and runs a little cooler, when running continuously. It is possible to run it on a longer extension cord (made up for 220, of course) without line loss being such an issue. I have made up an assortment of pigtails to plug into dryer outlets, and welder outlets. Yes, it is not protecting at the correct amps, but monitored, it is not much of an issue, I think. A dead short will still kick even a 50 amp breaker. If yours is like mine, it pulls almost 15 amps running, and more at start. It is necessary to have it's own circuit, if you want to run much else with it on the same circuit. My vote? Put up with the inconvenience (at times when you are using it away from the shop) and run it on 220. It should last longer, and be happier. The wire configuration for both voltages should be pictured on the data plate, or on the cover where the terminals are, that need to be changed. -- Posted via a free Usenet account from http://www.teranews.com |
#17
|
|||
|
|||
![]()
On Fri, 17 Nov 2006 22:59:28 -0600, Andy Asberry
wrote: On Fri, 17 Nov 2006 19:08:34 -0800, John Ammeter wrote: Why does everyone think the voltage is 110/220?? If that actually was the voltage you had in your house you'd be very unhappy. The nominal voltage is 118/236 with a +/- 5% range so you can see that 110/220 is actually outside the acceptable range. John I remember back in the fifties in vo-ag farm electrification class, it was emphasized that you should make sure light bulbs were labeled for 120 volt. Perhaps prior to that they were rated 110 or 115? Maybe that was the line voltage then. What is your take on it? --Andy Asberry recommends NewsGuy-- Ontario rural electrification was 135 in the sixties. Urban bulbs didn't last long if you were on a short line. This was done to make sure there was a minimum 110 at the end of the line. Not every farm had it's own transformer back then. -- Posted via a free Usenet account from http://www.teranews.com |
#18
|
|||
|
|||
![]() "John Ammeter" wrote What do you think happens when you operate a 240 volt device on 208 volts?? Lower than rated HP produced, and shorter than normal motor life. Plus, when you load the motor close to it's limits, the thermal protection or the breakers kick off. A real pain in the arse. For those that do not remember, I'm a carpentry teacher at a high school. I have the 208 single phase power, and prior to me getting there, people bought 220 large power tools, instead of 208. It makes a big difference. I make sure I order 208 equipment, and things are much happier. -- Jim in NC |
#19
|
|||
|
|||
![]()
Did you ever have your linemen wire up the tickler backwards?? That
gets real interesting when the voltage should be 240/480 open delta. I had a job where they needed 3 phase for the elevator and only delta was provided. Thank God it was a 120/240 system because when I wiggied the voltage at the socket I found over 420 volts (I don't recall the exact voltage) from one leg to the other. If it had been a 240/480 service that would have been 840 volts... considered "high voltage" and decidedly dangerous to the operator, namely ME. I was actually a radio and tv broadcast tech, and was lucky enough to never encounter that problem. I say lucky enough because, although we had no authorization to work on the main wiring of the buildings, there were opportunities for errors inside our equipment--especially the transmitters. We tried to be VERY carefull working in there; as the power supplies were well into the thousands of volts DC, and both accidents and close calls had occurred in the past. The open-delta problem had been solved by my predecessor at my first position as cheif operator, and had caused major reliability problems with the transmitting equipment until a third transformer was added. He had also organized a local society of engineers during that same period of time; which may have been a related fact since the effect of a long run of open-delta had to seem esoteric to the comptroller when he requested funds to "purchase" the additional transformer--which would have been roughly equal to the price of a new car. Peter |
#20
|
|||
|
|||
![]()
In article ,
John Ammeter wrote: Why does everyone think the voltage is 110/220?? Because that *is* what it 'used to be'. If that actually was the voltage you had in your house you'd be very unhappy. The nominal voltage is 118/236 with a +/- 5% range so you can see that 110/220 is actually outside the acceptable range. Over the years, the 'standard' has changed. *Several* times. 110V 115V 117V 120V were _all_ the 'standard' over the years -- I have pieces of equipment with all those voltages on the manufacturer's 'plate'. In 'common'/casual usage, even when the 'standard' was 115V or 117V, it was frequently referred to as "110V". In part because of 'mental inertia' -- the standard had been 110V for a lot of years before the 'nominal' network voltage was raised to 115V. And it wasn't all that many years before the 'standard' went to 117V, and then on to 120V. Essentially, it is a 'class label', not an exact value. ![]() There's even _more_ 'inertia' with regard to naming of the "2 hots, 180 degree out-of-phase" voltage level. It is *still* not infrequently referred to as "220" even though the actual line voltage has been much closer to 240 for 30+ years. A lot of people don't even recognize the inconsistency of referring to '1 hot' as 120V, and '2 hot' as 220V. The 'silliness' continues at the next higher voltage step. 'plates' on gear will likely state (correctly) 480V, but calling it '440V' is still _very_ common. "commonly accepted wisdom" is that 110V, 115V, 117V, and 120V all refer to the same thing, and similarly for 220V, 230V, and 240V. It's similar to the "fact" that a "12 V battery" typically puts out 13.6V. |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
Japanese firm sold Libya uranium conversion plant | Dav1936531 | Military Aviation | 2 | March 17th 04 03:47 PM |
PIREP: Headsets Inc conversion of Dave Clark DC10-13.4s | Paul Tomblin | Piloting | 0 | January 20th 04 01:46 PM |
Mini 500, Helicycle, Turbine, Joe Rinke, Rinke Aerospace, Rick Stitt, Conversion, Kit | TurbineMini Richard | Rotorcraft | 0 | January 15th 04 11:48 PM |
TRUTH OF THE MINI-500 TURBINE CONVERSION | Dennis Chitwood | Rotorcraft | 10 | January 7th 04 05:33 PM |
Auto conversion cost post | Richard Riley | Home Built | 13 | December 28th 03 12:52 PM |